Started by Medeek, February 11, 2013, 10:45:34 PM

Previous topic - Next topic

0 Members and 1 Guest are viewing this topic.

Medeek

Seems like sometimes you need to read between the lines with the code.  One thing I just realized is that the requirement to sheath the interior wall with Gypsum does not apply to certain bracing methods (ie. PFH, ABW).  So my assumption is that the penalty you normally take in calculating the wind and seismic factors with the gypsum omitted goes away with this type of bracing.  Updated calculations for all braced walls show below. 



Based on these calculations the only modification required to the plan is to increase the length of the interior braced wall(s) from 48" to 54" in order to get my 9ft of braced wall panel, originally this was 8ft of braced wall panel.  8ft will pass the seismic requirement but not the wind load.  Initially I thought the seismic loads would dominate with this analysis since I was shooting for SDC D2 but after applying the adjustment factors for the wind it became clear that the wind was just as much a problem.  The reasons for this are: 12/12 pitch of this roof (think large sail), tall wall (10ft), high basic wind speed, large open interior, and high exposure all compound together to make the wind a major factor in the bracing requirements.

Braced Wall Plan below:


Nathaniel P. Wilkerson, P.E.