Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

Wind Load Report - Campus Corner_Wind Calcs

1. Site & Building Data

Roof Type: Gable  
Wind Speed (ult): 100 mph
Exposure Category: B  
Enclosure Class: Enclosed  
Building Width (W): 30 ft.
Building Length (L): 48 ft.
Eave Height (he): 10 ft.
Foundation Height (hf): 0 ft.
Roof Pitch: 4 /12
Eave Overhang (OHe): 1 ft.
Gable Overhang (OHg): 1 ft.

2. Parameters & Coefficients

Topographic Factor (Kzt): 1.0
Directionality Factor (Kd): .85
Roof Angle (θ): 18.43 deg.
Mean Roof Height (h): 12.50 ft.
Ridge Height (hr): 15.00 ft.
Pos. Internal Pressure (+GCpi): +0.18  
Neg. Internal Pressure (-GCpi): -0.18  
Velocity Pressure Exp. Coeff. (Kh): 0.70 @ z=h
Velocity Pressure (qh): 15.24 psf
End Zone Width (a): 3.00 ft.
Zone 2/2E Dist.: 15.00 ft.

3. Design Assumptions and Notes

Code Standard: ASCE 7-10
Geometry: Regular-Shaped Bldg.
Height Class: Low-Rise Building
Notes: CD SET CALCULATIONS

4. Design Loads

Top Chord Dead Load: 8 psf
Bottom Chord Dead Load: 10 psf
Truss/Rafter Spacing: 24 in. o/c

4. Design Wind Pressures: MWFRS Envelope Procedure


Load Case A: Transverse Direction
Surface GCpf Design Pressure (psf)
(w/ +GCpi) (w/ -GCpi)
1 0.52 5.13 10.62
2 -0.69 -13.26 -7.77
3 -0.47 -9.89 -4.40
4 -0.42 -9.08 -3.59
1E 0.78 9.15 14.64
2E -1.07 -19.06 -13.57
3E -0.67 -13.01 -7.52
4E -0.62 -12.17 -6.68
2OH -0.69 -10.52
2EOH -1.07 -16.31
3OH -0.47 -7.14
3EOH -0.67 -10.26
2OH+W -0.69/-0.7 -21.19
2EOH+W -1.07/-0.7 -26.98
a) (+) and (-) signs signify wind pressures acting toward & away from surfaces.
b) External Pressure Coefficients linearly interpolated from Fig. 28.4-1 ASCE 7-10.
c) Design building for all wind directions, 4 load patterns per load case.
d) Total horizontal shear shall not be less than that by neglecting roof wind forces.
e) Min. wind load for enclosed or partially enclosed bldg.: 16 psf wall, 8 psf roof.
f) Design pressures are for strength design, multiply by 0.6 for ASD.
Wind Loads Troy Martinez 1501 Chrisway Drive 26 006
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-
4/26/2026 1
Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

Load Case B: Longitudinal Direction
Surface GCpf Design Pressure (psf)
(w/ +GCpi) (w/ -GCpi)
1 -0.45 -9.60 -4.12
2 -0.69 -13.26 -7.77
3 -0.37 -8.38 -2.90
4 -0.45 -9.60 -4.12
5 0.40 3.35 8.84
6 -0.29 -7.17 -1.68
1E -0.48 -10.06 -4.57
2E -1.07 -19.06 -13.57
3E -0.53 -10.82 -5.34
4E -0.48 -10.06 -4.57
5E 0.61 6.56 12.04
6E -0.43 -9.30 -3.81
2OH -0.69 -10.52
2EOH -1.07 -16.31
3OH -0.37 -5.64
3EOH -0.53 -8.08
2EOH+W -1.07/-0.7 -26.98
3EOH+W -0.53/-0.7 -18.75
a) (+) and (-) signs signify wind pressures acting toward & away from surfaces.
b) External Pressure Coefficients linearly interpolated from Fig. 28.4-1 ASCE 7-10.
c) Design building for all wind directions, 4 load patterns per load case.
d) Total horizontal shear shall not be less than that by neglecting roof wind forces.
e) Min. wind load for enclosed or partially enclosed bldg.: 16 psf wall, 8 psf roof.
f) Design pressures are for strength design, multiply by 0.6 for ASD.


Torsional Load Cases
Surface Load Case GCpf Design Pressure (psf)
(w/ +GCpi) (w/ -GCpi)
1T A - 1.28 2.65
2T A - -3.32 -1.94
3T A - -2.47 -1.10
4T A - -2.27 -0.90
5T B - 0.84 2.21
6T B - -1.79 -0.42
a) (+) and (-) signs signify wind pressures acting toward & away from surfaces.
b) Pressures designated with a "T" are 25% of full design wind pressures.
c) Torsional loading shall apply to all 8 load patterns using the figures shown.
d) Design pressures are for strength design, multiply by 0.6 for ASD.
e) Torsional Design Exceptions: One story bldg. with h ≤ 30 ft,
   Two stories or less framed with light frame construction,
   Two stories or less with flexible diaphragms.
Wind Loads Troy Martinez 1501 Chrisway Drive 26 006
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-
4/26/2026 2
Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

5. Wind Load Calculations


1.) Lateral Loads - Transverse Direction:


Lateral Loads on Roof Diaphragm with Positive Internal Pressure
48 ft.
6.00 ft.
42.00 ft.
36.5 plf
27.2 plf
27.4 plf
15.4 plf
763 lbs
704 lbs
39.0 plf
29.7 plf
57.2 plf
39.8 plf
48.9 plf
31.6 plf
5.4 plf
4.2 plf
30.8 plf
21.4 plf
2.1 plf
1.4 plf
1 ft.
1 ft.
a) (-) signs signify wind lateral forces acting opposite to the direction of the arrows shown.
b) Strength design values multiplied by 0.6 to obtain ASD values.



Wind Base Shear (ASD)
Load Case A: Transverse Direction
Load Case Walls (lbs) Roof (lbs) Roof Overhangs (lbs) Total Lateral Load (lbs) R1 (lbs) R2 (lbs)
Positive Internal Pressure 2174 -534 -172 1467 763 704
Negative Internal Pressure 2174 -534 -172 1467 763 704
Roof Pressure = 0 2174 0 0 2174 1143 1031
Min. Pressures (8 psf, 16 psf) 2304 1152 128 3584 1792 1792
a) Bottom half of wall neglected in tributary area calculations.
b) Strength design values multiplied by 0.6 to obtain ASD values.
Wind Loads Troy Martinez 1501 Chrisway Drive 26 006
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-
4/26/2026 3
Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

2.) Lateral Loads - Longitudinal Direction:


Lateral Loads on Roof Diaphragm with Positive Internal Pressure
30 ft.
3.00 ft.
27.00 ft.
27.9 plf
21.5 plf
19.7 plf
10.1 plf
14.3 lbs
75.7 lbs
151.5 lbs
236.7 lbs
760 lbs
713 lbs
a) (-) signs signify wind lateral forces acting opposite to the direction of the arrows shown.
b) Strength design values multiplied by 0.6 to obtain ASD values.
c) Where the length of building (L) exceeds 4X the mean roof height (h), wind drag forces should additionally be considered.



Wind Base Shear (ASD)
Load Case B: Longitudinal Direction
Load Case Walls (lbs) Gable Ends (lbs) Roof (lbs) Total Lateral Load (lbs) RA (lbs) RB (lbs)
Positive Internal Pressure 995 478 0 1473 760 713
Negative Internal Pressure 995 478 0 1473 760 713
Roof Pressure = 0 995 478 0 1473 760 713
Min. Pressures (8 psf, 16 psf) 1440 720 0 2160 1080 1080
a) Bottom half of wall neglected in tributary area calculations.
b) Strength design values multiplied by 0.6 to obtain ASD values.
Wind Loads Troy Martinez 1501 Chrisway Drive 26 006
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-
4/26/2026 4
Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

3.) Roof Truss Reactions:


Roof Truss/Rafter Reactions: Transverse End Zone
7 lbs
-69 lbs
Max. Horz. ① = 53 lbs
Max. Uplift ① = 7 lbs
a) Strength design values multiplied by 0.6 to obtain ASD values.
b) Windward loads may be positive or negative depending on pitch of roof.



Roof Truss/Rafter Reactions (ASD)
w/ Positive Internal Pressure
Load Case Horizontal Load (lbs) Gross Uplift (lbs) Net Uplift (lbs) U1 (lbs) U2 (lbs)
Transverse Int. Zone 26 451 -233 -93 -140
Transverse End Zone 43 622 -62 7 -69
Longitudinal Int. Zone 31 409 -275 -112 -162
Longitudinal End Zone 53 567 -117 -16 -101
a) Gross Uplift calculations do not include any counteracting roof dead loads.
b) Net Uplift calculations include counteracting roof dead loads multiplied by 0.6 per load case (7) ASCE 7-10.
c) Strength design values multiplied by 0.6 to obtain ASD values for wind loads.
d) Loads based on truss spacing calculated at 24" o/c.
e) Negative values for horizontal load indicate load acting in windward direction (tranverse load cases).
f) Negative values for uplift indicate net downward force (zero uplift).













*Disclaimer: The calculations produced herein are for initial design and estimating purposes only. The calculations and drawings presented do not constitute a fully engineered design. All of the potential load cases required to fully design an actual structure may not be provided by this calculator. For the design of an actual structure, a registered and licensed professional should be consulted as per IRC 2012 Sec. R802.10.2 and designed according to the minimum requirements of ASCE 7-10. The wind load calculations provided by this online tool are for educational and illustrative purposes only. Medeek Design assumes no liability or loss for any designs presented and does not guarantee fitness for use.
Wind Loads Troy Martinez 1501 Chrisway Drive 26 006
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-