Wind Load Report

1. Site & Building Data

Roof Type: Gable  
Wind Speed (ult): 115 mph
Exposure Category: C  
Enclosure Class: Enclosed  
Building Width (W): 32.3 ft.
Building Length (L): 68 ft.
Eave Height (he): 19 ft.
Foundation Height (hf): 0 ft.
Roof Pitch: 6 /12
Eave Overhang (OHe): 2 ft.
Gable Overhang (OHg): 2 ft.

2. Parameters & Coefficients

Topographic Factor (Kzt): 1.0
Directionality Factor (Kd): .85
Roof Angle (θ): 26.57 deg.
Mean Roof Height (h): 23.04 ft.
Ridge Height (hr): 27.07 ft.
Pos. Internal Pressure (+GCpi): +0.18  
Neg. Internal Pressure (-GCpi): -0.18  
Velocity Pressure Exp. Coeff. (Kh): 0.93 @ z=h
Velocity Pressure (qh): 26.74 psf
End Zone Width (a): 3.00 ft.
Zone 2/2E Dist.: 16.15 ft.

3. Design Assumptions and Notes

Code Standard: ASCE 7-10
Geometry: Regular-Shaped Bldg.
Height Class: Low-Rise Building
Notes:

4. Design Loads

Top Chord Dead Load: 7 psf
Bottom Chord Dead Load: 10 psf
Truss/Rafter Spacing: 24 in. o/c

4. Design Wind Pressures: MWFRS Envelope Procedure


Load Case A: Transverse Direction
Surface GCpf Design Pressure (psf)
(w/ +GCpi) (w/ -GCpi)
1 0.55 9.89 19.51
2 -0.10 -7.46 2.16
3 -0.45 -16.77 -7.14
4 -0.39 -15.26 -5.63
1E 0.73 14.65 24.27
2E -0.19 -9.90 -0.27
3E -0.58 -20.45 -10.83
4E -0.53 -19.12 -9.49
2OH -0.10 -2.65
2EOH -0.19 -5.09
3OH -0.45 -11.96
3EOH -0.58 -15.64
2OH+W -0.10/-0.7 -20.62
2EOH+W -0.19/-0.7 -23.06
a) (+) and (-) signs signify wind pressures acting toward & away from surfaces.
b) External Pressure Coefficients linearly interpolated from Fig. 28.4-1 ASCE 7-10.
c) Design building for all wind directions, 4 load patterns per load case.
d) Total horizontal shear shall not be less than that by neglecting roof wind forces.
e) Min. wind load for enclosed or partially enclosed bldg.: 16 psf wall, 8 psf roof.
f) Design pressures are for strength design, multiply by 0.6 for ASD.
Wind Loads Hoover
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-
2/9/2026 1
Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

Load Case B: Longitudinal Direction
Surface GCpf Design Pressure (psf)
(w/ +GCpi) (w/ -GCpi)
1 -0.45 -16.85 -7.22
2 -0.69 -23.26 -13.64
3 -0.37 -14.71 -5.08
4 -0.45 -16.85 -7.22
5 0.40 5.88 15.51
6 -0.29 -12.57 -2.94
1E -0.48 -17.65 -8.02
2E -1.07 -33.42 -23.80
3E -0.53 -18.98 -9.36
4E -0.48 -17.65 -8.02
5E 0.61 11.50 21.12
6E -0.43 -16.31 -6.68
2OH -0.69 -18.45
2EOH -1.07 -28.61
3OH -0.37 -9.89
3EOH -0.53 -14.17
2EOH+W -1.07/-0.7 -47.33
3EOH+W -0.53/-0.7 -32.89
a) (+) and (-) signs signify wind pressures acting toward & away from surfaces.
b) External Pressure Coefficients linearly interpolated from Fig. 28.4-1 ASCE 7-10.
c) Design building for all wind directions, 4 load patterns per load case.
d) Total horizontal shear shall not be less than that by neglecting roof wind forces.
e) Min. wind load for enclosed or partially enclosed bldg.: 16 psf wall, 8 psf roof.
f) Design pressures are for strength design, multiply by 0.6 for ASD.


Torsional Load Cases
Surface Load Case GCpf Design Pressure (psf)
(w/ +GCpi) (w/ -GCpi)
1T A - 2.47 4.88
2T A - -1.87 0.54
3T A - -4.19 -1.79
4T A - -3.81 -1.41
5T B - 1.47 3.88
6T B - -3.14 -0.74
a) (+) and (-) signs signify wind pressures acting toward & away from surfaces.
b) Pressures designated with a "T" are 25% of full design wind pressures.
c) Torsional loading shall apply to all 8 load patterns using the figures shown.
d) Design pressures are for strength design, multiply by 0.6 for ASD.
e) Torsional Design Exceptions: One story bldg. with h ≤ 30 ft,
   Two stories or less framed with light frame construction,
   Two stories or less with flexible diaphragms.
Wind Loads Hoover
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-
2/9/2026 2
Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

5. Wind Load Calculations


1.) Lateral Loads - Transverse Direction:


Lateral Loads on Roof Diaphragm with Positive Internal Pressure
68 ft.
6.00 ft.
62.00 ft.
109.0 plf
87.0 plf
83.5 plf
56.3 plf
6643 lbs
6323 lbs
99.1 plf
81.2 plf
48.0 plf
36.2 plf
24.7 plf
12.8 plf
13.8 plf
12.4 plf
75.8 plf
57.9 plf
9.4 plf
7.2 plf
2 ft.
2 ft.
a) (-) signs signify wind lateral forces acting opposite to the direction of the arrows shown.
b) Strength design values multiplied by 0.6 to obtain ASD values.



Wind Base Shear (ASD)
Load Case A: Transverse Direction
Load Case Walls (lbs) Roof (lbs) Roof Overhangs (lbs) Total Lateral Load (lbs) R1 (lbs) R2 (lbs)
Positive Internal Pressure 10040 3102 -176 12966 6643 6323
Negative Internal Pressure 10040 3102 -176 12966 6643 6323
Roof Pressure = 0 10040 0 0 10040 5154 4886
Min. Pressures (8 psf, 16 psf) 6202 2636 501 9338 4669 4669
a) Bottom half of wall neglected in tributary area calculations.
b) Strength design values multiplied by 0.6 to obtain ASD values.
Wind Loads Hoover
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-
2/9/2026 3
Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

2.) Lateral Loads - Longitudinal Direction:


Lateral Loads on Roof Diaphragm with Positive Internal Pressure
32.3 ft.
3.00 ft.
29.30 ft.
93.0 plf
71.6 plf
65.5 plf
33.5 plf
37.5 lbs
218.3 lbs
478.5 lbs
721.8 lbs
2585 lbs
2428 lbs
a) (-) signs signify wind lateral forces acting opposite to the direction of the arrows shown.
b) Strength design values multiplied by 0.6 to obtain ASD values.
c) Where the length of building (L) exceeds 4X the mean roof height (h), wind drag forces should additionally be considered.



Wind Base Shear (ASD)
Load Case B: Longitudinal Direction
Load Case Walls (lbs) Gable Ends (lbs) Roof (lbs) Total Lateral Load (lbs) RA (lbs) RB (lbs)
Positive Internal Pressure 3557 1456 0 5013 2585 2428
Negative Internal Pressure 3557 1456 0 5013 2585 2428
Roof Pressure = 0 3557 1456 0 5013 2585 2428
Min. Pressures (8 psf, 16 psf) 2946 1252 0 4198 2099 2099
a) Bottom half of wall neglected in tributary area calculations.
b) Strength design values multiplied by 0.6 to obtain ASD values.
Wind Loads Hoover
Engineer Company Name
123 Street City, State 12345
ph. (888) 777-5555    www.website.com
-
2/9/2026 4
Subject
Customer
Location
Job No.
Engr.
Rev.
Date
Page

3.) Roof Truss Reactions:


Roof Truss/Rafter Reactions: Transverse End Zone
-65 lbs
18 lbs
Max. Horz. ① = 157 lbs
Max. Uplift ① = 283 lbs
a) Strength design values multiplied by 0.6 to obtain ASD values.
b) Windward loads may be positive or negative depending on pitch of roof.



Roof Truss/Rafter Reactions (ASD)
w/ Positive Internal Pressure
Load Case Horizontal Load (lbs) Gross Uplift (lbs) Net Uplift (lbs) U1 (lbs) U2 (lbs)
Transverse Int. Zone -80 548 -181 -124 -56
Transverse End Zone -93 681 -47 -65 18
Longitudinal Int. Zone 93 804 75 90 -15
Longitudinal End Zone 157 1118 390 283 107
a) Gross Uplift calculations do not include any counteracting roof dead loads.
b) Net Uplift calculations include counteracting roof dead loads multiplied by 0.6 per load case (7) ASCE 7-10.
c) Strength design values multiplied by 0.6 to obtain ASD values for wind loads.
d) Loads based on truss spacing calculated at 24" o/c.
e) Negative values for horizontal load indicate load acting in windward direction (tranverse load cases).
f) Negative values for uplift indicate net downward force (zero uplift).













*Disclaimer: The calculations produced herein are for initial design and estimating purposes only. The calculations and drawings presented do not constitute a fully engineered design. All of the potential load cases required to fully design an actual structure may not be provided by this calculator. For the design of an actual structure, a registered and licensed professional should be consulted as per IRC 2012 Sec. R802.10.2 and designed according to the minimum requirements of ASCE 7-10. The wind load calculations provided by this online tool are for educational and illustrative purposes only. Medeek Design assumes no liability or loss for any designs presented and does not guarantee fitness for use.